    Question

    I WANT TO RUN 14/2 TECK CABLE UNDERGROUND, UNDERNEATH RAILROAD TRACKS. HOW FAR BELOW GRADE DO I NEED TO BE?

  2. #2
    HB Forum Owner electric-ed's Avatar
    Join Date
    November 17th, 2001
    Posts
    191
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    Table 53 says 600mm for 750 volts or less, and 1000mm for over 750 volts.

    I would check with the railroad. They may have rules for installeations on their right-of-way.

    I just thought, perhaps you work for the RR?

    Ed