October 31st, 2004, 10:24 PM
#1
Inactive Member
I WANT TO RUN 14/2 TECK CABLE UNDERGROUND, UNDERNEATH RAILROAD TRACKS. HOW FAR BELOW GRADE DO I NEED TO BE?
-
October 31st, 2004, 11:49 PM
#2
HB Forum Owner
Table 53 says 600mm for 750 volts or less, and 1000mm for over 750 volts.
I would check with the railroad. They may have rules for installeations on their right-of-way.
I just thought, perhaps you work for the RR?
Ed